19 февр. 2021 г. · 1.25" minimum conduit would be needed with Sch40 PVC. Long sweeps are probably not necessary. If you use Sch80 PVC you would need to use 1.5".
4 янв. 2020 г. · Wire sizes · 100A is #3 copper ($600/100ft) or #1 aluminum ($175/100ft). · 125A is #1 copper or #1/0 aluminum (you need to call it 120A feeder, ...
30 июл. 2024 г. · Use 3 aluminum 1 AWG wires for hot/hot/neutral. Use either 8 AWG copper or 6 AWG aluminum for the ground wire.
29 авг. 2018 г. · The appropriate wire sizing for this 125A feeder is 1/0 AWG aluminum or 2AWG copper, with XHHW-2 insulation either way, for the hots and neutral ...
18 окт. 2022 г. · Part 3: Size that feeder! · 21-90A: 2 AWG aluminum · 91-100A: 1 AWG aluminum · 101-120A: 1/0 AWG aluminum · 121-135A: 2/0 AWG aluminum.
15 февр. 2023 г. · One popular size is 2-2-2-4 aluminum which is good for 90A. That satisfies almost any imaginable need, including virtually all multi-car EV ...
18 мая 2024 г. · To calculate the minimum wire size for 125A we look at table 310.16, your terminations are rated at 75°C column, we look down that column and ...
27 февр. 2023 г. · You can use a 200A panel, so long as the feed breaker on the main supply size fits the wire you are using (90A or less) - your inspector is ignorant.
25 авг. 2020 г. · The answer is yes you can feed a 125 amp panel with 14 gauge Wire and a 15 amp breaker but that would be silly. We need to know your loads ...
16 авг. 2023 г. · It will only be a 4" slab, which I'm told will only be fiberglass reinforced so that may cause a snag in that idea. The concrete guys say ...