6 авг. 2005 г. · Re: 125 amp sub panel. Most likely I would choose 2 AWG copper. 2 AWG CU is rated 115 amp use 240.4(B) move up to next standard size OCP. |
28 апр. 2017 г. · The minimum permitted conductor would be #1/0 Al with a 125 OCPD. At 90 amps of load your voltage drop would still be under the 3% recommended ... |
26 мар. 2021 г. · Is there just the one 125 amp service disconnect feeding this one panel ? If so, a #2 Cu or 1/0 AL will work. |
A 125 amp subpanel require a 1/0 feeder, the client is installing a undersized feeder to supply only the total amp he will be using. |
26 апр. 2007 г. · One way to do this is to splice the #4/0 with a 125A rated wire before coming into the panel, so he can connect to the panel with no problems. |
25 сент. 2021 г. · I am also installing a 125 amp sub panel, 1/0 SER has 120 amps in the 60 degree column. But I dont know if a 120 breaker exists, so I can use ... |
6 окт. 2018 г. · The OP's question was can you use the #2-3 NM for a 125A subpanel. I see no problem with feeding a 125A subpanel with #2-3 NM as long as the ... |
6 февр. 2021 г. · Hello all. I'm running #3 thhn for a 125 amp pool sub panel. I was wondering if I could run #6 thhn for the ground and nuetral wires. |
25 авг. 2017 г. · #4 copper is good for 85 amps which means that you can go up to the next standard size which is 90 amps. If you want to use a 100 amp OCPD you will need to ... |
Novbeti > |
Axtarisha Qayit Anarim.Az Anarim.Az Sayt Rehberliyi ile Elaqe Saytdan Istifade Qaydalari Anarim.Az 2004-2023 |