8 июн. 2017 г. · 250.66(A) says the grounding electrode to a single or multiple rods shall not be required to be larger than a #6 copper wire. |
10 июн. 2008 г. · There is a argument that you must use a #4 bare copper minimum to both ground rods for a 200 amp service. |
26 июл. 2014 г. · In Table 250.66, it lists a 4 AWG copper grounding conductor for 2/0 copper or 4/0 aluminum service conductors, which are the sizes used for ... |
28 янв. 2010 г. · The required size of the grounding electrode conductor is based on the size of the largest ungrounded service entrance conductor. |
9 апр. 2021 г. · Assuming the neutral is a CCC any applying adjustment factors we come up with 10 Sets of 4/C 750MCM for service entrance. Existing installation ... |
Most often that would end up being a 1/0 cu. #6 is the max you need to ground rods and #4 the max to concrete encased electrodes. The location of the connection ... |
5 апр. 2020 г. · Table 250.122 tells you that 10AWG equipment grounding conductor is good for up to 60A. Put 6AWG on a 50A breaker and all you need is a 10AWG ... |
Some utilities require a #4 Cu ground wire here in IN. for a 200 amp house service. But I thought #6 is all the bigger it needs to be. |
16 мар. 2006 г. · I am doing a 200 amp sub feed in a residential home. Normally I would run aluminum SER cable which has three 4/O (2 hots, a neutral, and a 2/O ... |